Question 9021 of 749 · Maryland Journeyperson Electrician Exam
At a motor fuel dispensing facility, how is the area up to 18 in above grade within 20 ft horizontally of a dispenser enclosure classified?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9021
- B: Class I, Division 2
Explanation
The table of classified locations for motor fuel dispensing makes the outdoor area up to 18 in above grade and within 20 ft horizontally of the dispenser enclosure a Class I, Division 2 location. Spaces inside the dispenser enclosure are Division 1.