Question 9025 of 871 · Maryland Journeyperson Electrician Exam
Beneath a classified area at a motor fuel dispensing facility, PVC conduit is permitted underground when buried with at least what cover, with threaded RMC or IMC used for the last section before emerging?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9025
- B: 2 ft
Explanation
Underground wiring below Class I locations at dispensing facilities is normally threaded RMC or IMC. PVC and similar nonmetallic conduit is allowed where buried under at least 2 ft of cover, with threaded RMC or IMC used for the last 2 ft before emerging and an equipment grounding conductor installed.
More questions: Special Occupancies
- 9026In a major repair garage for gasoline vehicles without the specified mechanical ventilation, how is the floor area up to 18 in above the floor classified?
- 9027The interior of a spray booth used for applying flammable paint is classified as which location?
- 9028In an aircraft hangar, the area up to 18 in above the hangar floor is classified as which location?
- 9029In health care facilities, a patient care space where failure of equipment or the electrical system is likely to cause major injury or death is which category?
- 9030A patient care space in which failure of equipment is likely to cause only minor injury to patients or caregivers is classified as which category?
- 9031Branch circuits serving patient care spaces must provide two equipment grounding paths. Which combination meets this requirement?