Question 9027 of 938 · Maryland Journeyperson Electrician Exam
The interior of a spray booth used for applying flammable paint is classified as which location?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9027
- C: Class I, Division 1 or Zone 1
Explanation
Article 516 classifies the interior of spray booths and rooms where flammable materials are sprayed as Class I, Division 1 or Zone 1. Ventilation affects the extent of surrounding Division 2 areas, but not the classification of the booth interior.
More questions: Special Occupancies
- 9028In an aircraft hangar, the area up to 18 in above the hangar floor is classified as which location?
- 9029In health care facilities, a patient care space where failure of equipment or the electrical system is likely to cause major injury or death is which category?
- 9030A patient care space in which failure of equipment is likely to cause only minor injury to patients or caregivers is classified as which category?
- 9031Branch circuits serving patient care spaces must provide two equipment grounding paths. Which combination meets this requirement?
- 9032The patient care vicinity extends horizontally 6 ft beyond the normal patient location and vertically to what height above the floor?
- 9033Each patient bed location in a Category 2 (general care) space must be provided with at least how many receptacles?